Discussion note on
Draft KERC (Forecasting, Scheduling, Deviation settlement and related
matters for Wind and Solar Generation sources) Regulations, 2015.
1.0.
Preamble:
a) The installed capacity of Renewable Energy generation in Karnataka
was 5068 MWs as on 31-03-2015, which accounts for 33.66% of the total
installed capacity of 15052 MW including the States share from CGS.
The installed capacity of wind generation is about 2400 MW accounting
to about 47.35 % of Renewable Energy generation and is about 15.94 %
of total installed capacity in the State.
b) A minimum load of 4125 MW was recorded in the State at about 3.0 AM
on 31-08-2014 (with a peak load of 5878 MW on the same day and the
peak demand of 9549 MW during FY-15). The wind generation was
maximum from 30th August, 2014 to 8th September, 2014. There was a
forced backing down of the wind generation ranging between 761 MW
to about 1742 MW during the maximum wind generation period to
maintain the frequency band within maximum permissible limit of 50.2
Hz, after taking all other possible measures like minimizing the thermal
and hydel generation. In spite of backing down the wind generation,
the RE generation was about 35 to 40 MU per day and wind generation
was about 17.96 MU to 27.80 MU per day during these days.
(The details are shown in annexure-A)
c) The installed capacity of solar generation in the State is about 83 MW
and about 800 - 1000 MW capacity is proposed to be added during
FY16 and FY17. A big solar generation park of 2000 MW is proposed to
be established in Pavagada Taluka of Tumukuru district.
d) Renewable energy generation (wind and others) in the southern region
as on 30-04-2015 was about 15117 MW which accounts for 23.20% of
1
duration of time are the two main concerns arising out of the variable
wind and solar generation.
g) Generation of power from wind and solar is totally influenced by the
nature, i.e. wind velocity and solar insolation, climatic changes and
geographical condition, which are difficult to accurately predict
/forecast.
h) In the last two years, many of the wind generation plants are backed
down in Karnataka during high wind and low load monsoon periods for
the grid operational issues of high system frequency. The problem will
become more acute during the subsequent years due to addition of
more wind and large scale solar power generators in Karnataka.
i) Adequate capacity of Hydro and Gas based generation capable of
responding to quick ramp up and
m) Recently, the CERC has issued the amendment to the CERC DSM and
related matter Regulations, 2014 for Forecasting, Scheduling and
Imbalance handling of interstate transactions of Wind and Solar
Generation.
n) Hence it is found necessary to formulate Karnataka Electricity
Regulatory Commission (Forecasting, Scheduling, Deviation settlement
and
related
matters
for
Wind
and
Solar
Generation
sources)
KEGC,
through
forecasting,
scheduling
and
commercial
3.0.
Forecasting Tools:
a) Renewable Energy Management Centres (REMCs):
REMS, equipped with advanced forecasting tools are being established
in the country for forecasting wind and solar generation.
b) M/s NIWE (National Institute of Wind Energy) have already taken up a
pilot study for wind forecasting
tools in all the wind mill locations in Tamil Nadu. The project envisages
installing of wind forecasting tools and also collecting live energy data
from wind energy pooling substations, installing equipments for real time
measurement of wind generation with communicative ABT meters in all
wind energy pooling substations and providing consolidated real time
wind energy data on a dash board installed at Central Station in
Chennai. In addition, the real time data will be fed into NIWEs
forecasting system that can be used for scheduling and forecasting wind
generation. The forecasting of 7480 MW wind installations is now
operational and made available to Tamil Nadu SLDC and it is learnt that
it is almost 85% near to actual.
4.0.
Draft Frame work for Forecasting, Scheduling & Handling deviations from
schedule for the infirm wind and solar generation.
4.1.
Applicability :
The proposed frame work is applicable to:
a) All Wind Generators having a combined installed capacity of 10.0
MW and above at the pooling station whether they are supplying
power to ESCOMs or to third party consumers through open access or
for captive consumption through open access within or outside the
State.
b) All Solar Generators with installed capacity of 5.0 MW and above at
the pooling station whether they are supplying power to ESCOMs or
5
Fore casting:
a)
of wind and
The existing wind and solar power plants shall either by themselves or
through Qualified Coordinating Agency (QCA) or through an
Aggregator shall establish forecasting tools within three months from
the effective date of these Regulations and for new wind and solar
generators they shall be established
plants.
c)
d)
4.3.
a) Schedule details:
i. The wind and solar power plants either by themselves or through
Qualified Coordinating Agency (QCA) or through an Aggregator shall
furnish weekly, day ahead and intraday generation schedules of 15
minutes interval block period to SLDC by using / establishing
appropriate forecasting tools at their Wind-farm /Solar facility.
ii. Forecasting and scheduling Point:
The forecasting and scheduling of wind and solar generators shall be
conducted at pooling station level which being a commercial metering
point, though the forecasting tools are installed at wind-farm/solar
facility.
6
b) Frequency of Revisions
Considering the fact that wind and solar generation is intermittent and
variable in nature and also taking into account the fact that accuracy of
forecast improves as we move closer in time, the Wind and Solar energy
generator shall be allowed more opportunities to revise the schedule. It is
therefore proposed to provide an opportunity to the Wind and Solar
generators to revise the day ahead schedules for a maximum of 16
revisions during the intraday, one each in one and half hour time slot
starting from 00:00 hours during the day with prior notice of at least 60
minutes for each revision.
c) The wind, solar power and other RES should be given first priority in
generation scheduling and dispatching under normal power system
operating conditions.
d) Grid operator (SLDC) should consider forecasted generation schedule of
wind and solar power in the midterm to long term, day-ahead and intraday operation planning processes of scheduling and fully make use of the
flexibility from conventional power plants, as well as the capacity of inter
grid tie-lines to accommodate the maximum wind and solar power while
maintaining system security and reliability.
e) The Principal generator/ QCA/ Aggregator
long-term
involved for
connectivity,
5.0.
6.0.
6.1.
Methodology to account for and settle the deviations by wind and solar
energy generators.
a) The day ahead scheduling in the country is being done for all interState schedules as per the Indian Electricity Grid Code on the basis of
15 minutes interval time blocks except for RES. The deviation between
schedule and actual power flow is called Unscheduled Interchange
(UI) for which commercial settlement is done as per the Unscheduled
Interchange (UI) rates specified by the Central Electricity Regulatory
Commission (CERC). The UI rates are variable depending on the
frequency and the quantum of drawal and they tend to discourage
over drawal and under generation. The day ahead schedules can
also be revised with prior notice of 60 minutes.
b) KERC vide ORDER No.B/09/5 dated 20th June 2006 have brought the
following Users and Generators in the State under intra State ABT
and deviation settlement mechanism:
c)
i.
ii.
iii.
iv.
v.
under
ABT
mechanism
and
deviation
settlement
6.2.
6.2.1. At present the wind, solar and other RES generators (excluding Bio-mass
and Co-generation plants of 25 MW & above) are exempted from the
purview of Unscheduled Interchange (UI) and Deviation Settlement
Mechanism (DSM) within the State.
6.2.2. The wind and solar generators are now proposed to be brought under
purview of DSM as detailed below:
a) The permissible deviation for all the wind and solar plants shall be
15 %
permissible limits
a) Wind and Solar
Sl
No
Particulars
Deviation range
with %
25 %
of energy
15 % and up to 25 %
schedule
10
and
for
supplying
to
power
15%)
consumers
availing
open
access
facilities
beyond
power
within
or > 25
35 %
of energy
15 % and up to 25
beyond
25 % & up to 35 %.
Rs 0.50 per kWh for the quantum
of short fall or excess of energy for
deviation from schedule beyond
15 % and up to 25 %
+ (plus) Rs 1.0.per
more
> 35 %
25 % up to 35 %
+ (plus) Rs 1.50
schedule
beyond 35 %
charges.
11
7.0.
8.0.
Grid
Strengthening
for
RES
Evacuation:
(Green
Corridor).
Provisions will be made in the Karnataka Electricity Grid Code 2005 for
identifying the constraints in evacuation of wind & solar power locally as
well as at grid level (upstream) during high wind and solar energy
penetration and low local loads and take immediate measures for
implementation of grid strengthening proposals by the Transmission utility.
9.0.
separate
regulations
called
Karnataka
Electricity
Regulatory
12
Annexure:
Sl No
Date
From
To
Maximum
Wind
Backing
Minimum
Down of the
Load
wind
Frequency
MW
generation in
HZ
during
the day
MW (installed
in
RE
Generation
during the
day in MU
geeration
during
the
day
in MU
capacity)
27-08-14
16.06 Hrs
19.06 Hrs
20
50.17
4636
34.98
17.96
30-08-14
23.24 Hrs
00.00 Hrs
760.96
50.12
4012
40.83
26.674
31-08-14
22.00 Hrs
00.00 Hrs
1063.2
50.3
4125
39.11
27.799
1/9/2014
00.30 Hrs
6.00 Hrs
855.03
50.23
4200
38.33
25.403
6/9/2014
23.10 Hrs
00.00 Hrs
845.58
50.13
5004
39.35
24.729
7/9/2014
00.00 Hrs
7.00 Hrs
1013.7
50.13
4713
34.25
18.686
8/9/2014
00.00 Hrs
6.00 Hrs
1741.99
50.12
4715
40.92
25.159
13
Annexure-B: Illustration for computation of deviation charges for wind and solar generators
Particulars
Unit
Scenario-3
Scenario-4
permissible
deviation range
%
of Rs
< than 15 %
deviations
Schedule
> 15 %
- >
25
< 25 %
< 35 %
kWh
1000
1000
1000
1000
kWh
900
800
700
600
of kWh
100
200
300
15 % of 1000 =150
energy
Actual
generation
Deviation
energy
quantum
% Deviation
< 25%
Quantum
of kWh
deviation for
which
Nil
up
to
15
% 200-150=50
<35%
300-150-100=50
400-150-100-100=50
ie 150
the
charges to be
levied
14
Rate of DSM Rs
Nil
charges
Rs
0.50
kWh
100
(250-150) 100
kWh
(250-150)
kWh
kWh
100
energy 1.50
400-350)for
deviation
to remaining
50 kWh
schedule
deviation
to
schedule
Permissible
kWh
15 % of 1000 =150
energy
15 % of 1000 =150
=150
deviation
Deviation
kWh
Nil
energy
(200-150)
50 kWh
above limits
DSM charges Rs
payable
by
Nil
50*0.5 = 25
[{(100*0.5}+
*1.0}]= 100
Generator
15